问答题 6分

Severity of explosions vary between a puff which may lift a relief valve to a violent explosions whi...

Severity of explosions vary between a puff which may lift a relief valve to a violent explosions which
causes major damage and may injure personnel and cause a fire. Evidence indicates that the longer the
combustion path, the more violent the explosion. This has become an area of concern with the large two
strokes of today which may have a crankcase volume of 500m3.
When an explosion occurs a flame front travels down the crankcase with a pressure wave in front of it.
The turbulence caused by moving engine components causing churning and mixing of vapors increase the
speed of the flame front and its area, which contribute to the increase in pressure. Turbulence caused by
venting of the pressure through relief valves can also influence the explosion.
Following the venting of the explosion through the relief valves, there is a drop in crankcase pressure
to below atmospheric pressure. This can cause air to enter the crankcase resulting in another flammable
mixture to be developed resulting in a secondary explosion to occur. The secondary explosion is more
violent and can result in crankcase doors being blown off the engine, and fires starting in the engine room.
If the relief valves do not reseal after lifting, or if they do not lift at all in the primary explosion ( due to
lack of maintenance etc), then door(s) may be blown off in the primary explosion, giving a ready path for
the ingress of air, which will make a secondary explosion more likely. Air can also be sucked in via the
crankcase vent, although rules state that this must be as small as practicable and new installations must
have a non return valve fitted.
If a primary explosion occurs, the pressure wave may send a large amount of oil mist out into the
engine room. Although the flame arrestors on the relief valves should prevent ignition of this oil mist by the
flame front, the mist will be sucked up towards the turbocharger where it may be ignited by an un-lagged
hot exhaust manifold. This ignition of oil mist can cause severe damage to plant and personnel.

你可能感兴趣的试题

5 问答题 6分
For a certain provision cooling plant, the capacity regulator is generally controlled depending on
pressure, temperature or relative humidity. The pulse emitter is therefore either a pressostat(压力继电器),
thermostat or hygrostat. The switching difference of the control units should be rated as large as possible.
This applies in particular to control by means of the pressure, because change to the load in the
refrigeration circuit results in relatively quick pressure changes compared to temperature, which can in turn
lead to inadmissible oscillation of the regulator.

Under partial load, the suction volume and thus the gas speed can undergo marked changes depending on the
regulation stage. For this reason, the rating and routing of the suction line must be given particular attention.
In order to guarantee sufficient oil return, neither full load nor partial load operation may allow the gas speed
to fall below a minimum level: 4 m/s in horizontal pipe sections; 8 m/s in vertical pipes.

For this reason we recommend that vertical pipes bestaggered into two separate sections (as illustration).
As a result of the falling suction gas speed velocity in partial load operation, the pipe elbow B is
blocked by an accumulation of oil. This increases the gas velocity in pipe section A. In order to guarantee adequate
oil return, both cross sections must be rated so large that the velocity does not fall below the minimum level
in full and partial load operation. In plants with extensive pipe systems it is recommended at least for R22 and NH3
to install an additional oil separator. This reduces the oil circulation period and can have positive effects above
all for cold starts with relatively high oil ejection.